Old 25th Jan 2021, 9:10 pm   #21
dglcomp
Heptode
 
Join Date: Jul 2016
Location: Portland, Dorset, UK.
Posts: 870
Default Re: Standardisation of Mains Voltages

Quote:
Originally Posted by G6Tanuki View Post
Quote:
Originally Posted by Brigham View Post
A decade or so later, the new workers' housing in nearby Billingham had AC at 40 cycles, unmetered, and included in your rent.
I remember that trains often used 80-Volt lightbulbs!
Going by what I've read on rail forums there were many different ways the bulbs would be wired too depending on where the power was derived from and I believe unpowered coaching stock, EMU's and DMU's all used different voltages. Also some bulbs were 3 lug BC to dissuade theft though I hate to think what would happen with an 80V bulb on 240V!, I would guess very bright for a second.
dglcomp is offline  
Old 25th Jan 2021, 9:37 pm   #22
Herald1360
Dekatron
 
Herald1360's Avatar
 
Join Date: Feb 2007
Location: Leominster, Herefordshire, UK.
Posts: 16,528
Default Re: Standardisation of Mains Voltages

Not quite as exciting as a 24V BA22D on 240V


Bulbs in our house were sometimes "liberated" from various sources
__________________
....__________
....|____||__|__\_____
.=.| _---\__|__|_---_|.
.........O..Chris....O
Herald1360 is offline  
Old 25th Jan 2021, 9:57 pm   #23
emeritus
Dekatron
 
Join Date: Jan 2012
Location: Brentwood, Essex, UK.
Posts: 5,316
Default Re: Standardisation of Mains Voltages

My understanding is that, before improved manufacturing techniques allowed filaments to be manufactured with closely-controlled resistances, bulbs were tested after manufacture and sorted according to the voltages they were suitable for.

My Victorian GEC catalogue includes an illustration of a bulb marked for 105V. I believe that early electric companies may have provided different voltages in cooperation with the bulb manufacturers to allow most of bulb production to be used. Before the invention of Dumet, part of the reason for the high cost of bulbs was that the only metal capable of wetting to glass to provide a hermetic seal and having a matched coefficient of thermal expansion was platinum. Things were different by the Edwardian era: by 1905 the manufacture of GEC's "Robertson" lamps included a semi-automated step of an operative immersing the mounted filament in bath of liquid benzene and applying current to make the immersed filament glow. As well as removing any localised thinner hot spots by depositing carbon, it allowed the manufacture of filaments with precisely-controlled resistances, current being automatically switched off when the required resistance had been reached. So there was then less need for lots of slightly different mains voltages to make use of bulb manufacturing spreads.

Last edited by emeritus; 25th Jan 2021 at 10:04 pm. Reason: Typos
emeritus is offline  
Old 25th Jan 2021, 10:08 pm   #24
paulsherwin
Moderator
 
paulsherwin's Avatar
 
Join Date: Jun 2003
Location: Oxford, UK
Posts: 27,787
Default Re: Standardisation of Mains Voltages

Of course, before the 1920s most domestic premises used gas or oil lighting, and electric light was a prestige thing for specialist applications. A few areas of central Oxford still used gas street lighting until the 1990s, and there are lots of other examples.
paulsherwin is offline  
Old 25th Jan 2021, 10:17 pm   #25
Dave Moll
Dekatron
 
Dave Moll's Avatar
 
Join Date: Feb 2005
Location: West Cumbria (CA13), UK
Posts: 6,118
Default Re: Standardisation of Mains Voltages

Quote:
Originally Posted by paulsherwin View Post
A few areas of central Oxford still used gas street lighting until the 1990s, and there were lots of other examples.
I certainly remember gas street lamps in the area of Headington (a suburb of Oxford) where I lived in the 1950s and 1960s. I don't recall when they were eventually replaced with electric ones as I moved away (to areas with no street lighting) at the start of the 1970s and only passed through thereafter.
__________________
Mending is better than Ending (cf Brave New World by Aldous Huxley)
Dave Moll is offline  
Old 25th Jan 2021, 10:32 pm   #26
Heatercathodeshort
Dekatron
 
Heatercathodeshort's Avatar
 
Join Date: Jun 2005
Location: Warnham, West Sussex. 10 miles south of DORKING.
Posts: 9,145
Default Re: Standardisation of Mains Voltages

Quote:
Originally Posted by JonSnell View Post
I grew up in the 50s and we had 220v DC until 1954.
I have a copy of 'The Practical Electrician's Pocket Book 1925 edition.

It lists Weymouth. Generating station owned by Corporation. Resident Engineers name, G. Nicholson. Voltage of supply, 230 & 460 DC.
Cost. Lighting, 7d. Heating and cooking, 2d. Power 2d and electric vehicle charging, 2d. [Old money 240d = £1]

It lists all the generating stations in England, Scotland, Wales and Ireland.

An incredible mixture of voltages frequencies and DC from 100v-250v with one entry for mining pumps at £6500v!

It must have been very difficult for radio dealers and in fact anyone dealing with electrical appliances as some streets had differing supplies in the same terrace of houses! John.
Heatercathodeshort is offline  
Old 25th Jan 2021, 10:53 pm   #27
Hartley118
Nonode
 
Hartley118's Avatar
 
Join Date: Aug 2015
Location: Cambridge, Cambs. UK.
Posts: 2,196
Default Re: Standardisation of Mains Voltages

Quote:
Originally Posted by paulsherwin View Post
DC mains came from a wide range of sources before the grid was established. Some towns had municipal power stations, but often the supply came from large local factories or mines, or even the local tram network. Some of these supplies must have been pretty noisy. They were mostly used to power lighting at first, so the noise wouldn't have mattered.
I recall working in Doncaster Power Station as a student trainee in 1962. The main supply to consumers was 240V AC, but in the old part of the Station, which looked like a fascinating museum, there were rotary converters to supply the DC requirements. One converter supplied the trolley buses and a second one supplied those consumers who still had a DC supply contract. AFAIR, the main DC user was the local printing works.

Martin
__________________
BVWS Member
Hartley118 is offline  
Old 27th Jan 2021, 12:49 pm   #28
chriswood1900
Octode
 
Join Date: Jan 2007
Location: Dorridge, West Midlands, UK.
Posts: 1,475
Default Re: Standardisation of Mains Voltages

Quote:
Originally Posted by Dai Corner View Post
I came across a thread in a Bristol-based history/nostalgia Group on Facebook in which members were discussing the change from 210v to 240v in the late 60s / early 70s. Apparently appliances were swapped out area by area and people moving house encountered difficulties if their kit was the wrong voltage for their new abode.

I'd have been about ten at the time and took a keen interest in all things electrical but have no recollection at all of this exercise, assuming it had been completed well before I was born in 1960.

Does anyone remember this? Did retailers have to stock two versions or reconfigure appliances before sale? Did they get involved in the swap-out process?

Did repairers have to check what their customers' supply voltage was and use transformers if their own was different? Did modifications bring them work?
I lived in Patchway Bristol at this time, we had moved there from the Forest of Dean where we had 240V, the Ekco TV and Ferguson radio could be adjusted to around 210 volt and worked OK most other things worked and just took longer to heat.
I have vague memory of an electrician from SWEB visiting and changing some appliances belonging to the landlord like the elements in the cooker and providing some spare bulbs dad changed the TV and radio back to 240V and we carried on, some older stuff like a free standing water heater were just left presumable to have a shortened life. Most of the changes were around 1965.
There was a previous post on this theme here https://www.vintage-radio.net/forum/...ad.php?t=41380
__________________
Chris Wood
BVWS Member
chriswood1900 is offline  
Old 27th Jan 2021, 1:09 pm   #29
electrogram
Heptode
 
Join Date: Jul 2008
Location: Hereford, UK.
Posts: 719
Default Re: Standardisation of Mains Voltages

#24, Still gas street lamps in parts of Malvern
electrogram is online now  
Old 27th Jan 2021, 5:07 pm   #30
Graham G3ZVT
Dekatron
 
Graham G3ZVT's Avatar
 
Join Date: May 2010
Location: Greater Manchester, UK.
Posts: 18,676
Default Re: Standardisation of Mains Voltages

1,500 gas lamps remain in London apparently.
https://www.ppsi.org.uk/ppsi_new/Exp...s%20Lights.pdf
__________________
--
Graham.
G3ZVT
Graham G3ZVT is offline  
Old 27th Jan 2021, 5:24 pm   #31
jjl
Octode
 
jjl's Avatar
 
Join Date: Jan 2003
Location: Ware, Herts. UK.
Posts: 1,082
Default Re: Standardisation of Mains Voltages

Quote:
Originally Posted by JonSnell View Post
Now they say we have a standard EU voltage of 230volts at 50HZ but it is actually 240v in the UK and 220volts in France.
When I lived in France for part of the time between 2004 and 2013 all appliances, bulbs etc. that I bought there were rated at 230V. On the odd occasion that I measured the mains voltage it was always in the low to mid 230s.

John
jjl is offline  
Old 27th Jan 2021, 5:37 pm   #32
broadgage
Nonode
 
Join Date: Jan 2010
Location: North Somerset, UK.
Posts: 2,129
Default Re: Standardisation of Mains Voltages

Quote:
Originally Posted by rambo1152 View Post
Quote:
Originally Posted by G6Tanuki View Post
I remember in the 60s a family-member living in Nottinghamshire had mains that was 200VDC, with the +ve pole earthed. The next-door house had 200VDC with -ve earthed
As I have no memory of ever seeing DC mains, I have some questions.
What sort of plug & socket was used?

Was it an advantage for a radio to be in a -ve earth house?

A set clearly won't work with the wrong polarity, but could any damage result?
(I'm thinking of a leaky metal rectifier).

There would be no hum, but were there any other, perhaps more annoying artefacts?

Thanks!
Various plugs and sockets were used on DC mains, but the most common were round pin types in one of the three standard sizes of 2 amp, 5 amp and 15 amp. DC socket outlets were required to have a switch.
Sockets on 200 volts to 250 volt DC circuits should preferably have been 3 pin with an earth, but not all were.
On 100 volt to 125 volt circuits earthing was a lower priority and 2 pun outlets were common.
13 amp fused plugs and sockets were not meant to be used on DC circuits.

A radio set should work equaly well on either polarity, most householders probably did not know or care if their supply was positive or negative.

A correctly functioning set, or one with a valve rectifier would suffer no harm if connected with the wrong polarity. A defective metal rectifier could blow up the smoothing cap and the rectifier.

DC supplies were generaly relatively smooth with little interference.
broadgage is offline  
Old 27th Jan 2021, 5:52 pm   #33
broadgage
Nonode
 
Join Date: Jan 2010
Location: North Somerset, UK.
Posts: 2,129
Default Re: Standardisation of Mains Voltages

Domestic supplies of less than 200 volts generally "went out with war" though a handful remained.
Radio and TV sets usualy had a tapped mains dropper resistance with several settings to cater for voltages between 200 and 250 volts.

Heaters and cookers were usually supplied in two versions, one for 200 volt to 220 volt circuits and another version for 230 volt to 250 volt circuits.

Light fitting were suitable for any reasonable voltage (unless fluorescent, still rare) Lamps had to be the correct voltage and the local electrical shop would stock a range.

Trains used various odd voltage lamps.
Trams used 110 volt lamps in series groups of 5 from the 550 volt supply.
Trolley buses used 34 volts from an on board converter.
broadgage is offline  
Old 27th Jan 2021, 6:27 pm   #34
emeritus
Dekatron
 
Join Date: Jan 2012
Location: Brentwood, Essex, UK.
Posts: 5,316
Default Re: Standardisation of Mains Voltages

Lynmouth had one of the last public sub-200V public supplies: 100VAC at 100Hz from a local generating station which was destroyed in the 1952 flood. It was mentioned in a thread here some years ago that Lynmouth was due to have been connected to the national grid the following year, so the flood brought it forward.

Last edited by emeritus; 27th Jan 2021 at 6:31 pm. Reason: Typos
emeritus is offline  
Old 27th Jan 2021, 6:38 pm   #35
G6Tanuki
Dekatron
 
G6Tanuki's Avatar
 
Join Date: Apr 2012
Location: Wiltshire, UK.
Posts: 13,953
Default Re: Standardisation of Mains Voltages

Quote:
Originally Posted by broadgage View Post
Various plugs and sockets wee used on DC mains, but the most common were round pin types in one of the three standard sizes of 2 amp, 5 amp and 15 amp. DC socket outlets were required to have a switch.
And the switch had to be a "Quick-Make-Break" [QMB] type - toggle- or snap-action - because unlike on AC working it couldn't depend on the-voltage-passing-through-zero-within-a-few-milliseconds to stultify any contact arcing, all the more-important when DC supplies fed a possibly-inductive load such as a motor.

Such switches - whether on sockets or light-switches or big metal-clad fuse-boxes - always changed-over with a distinct and satisfying clunk/clang/click. Modern "AC Only" switches just use a cam-and-rocker mechanism which lack the quick-contact-separation mechanism with its reassuring audio-feedback.
G6Tanuki is offline  
Old 27th Jan 2021, 6:48 pm   #36
Electronpusher0
Nonode
 
Join Date: Jun 2016
Location: Bognor Regis, West Sussex, UK.
Posts: 2,288
Default Re: Standardisation of Mains Voltages

Quote:
Originally Posted by G6Tanuki View Post
I remember in the 60s a family-member living in Nottinghamshire had mains that was 200VDC, with the +ve pole earthed.

My father, who was born in 1923, used to recall that as a child his house in Littlehampton was fed from DC, he recalled the lights pulsing slightly from the slow revving generator.
The generator was situated in Duke Street, the site now houses an electricity sub station.

Peter
Electronpusher0 is offline  
Old 27th Jan 2021, 7:17 pm   #37
broadgage
Nonode
 
Join Date: Jan 2010
Location: North Somerset, UK.
Posts: 2,129
Default Re: Standardisation of Mains Voltages

Indeed, generators driven by low speed reciprocating engines tend to produce a pulsating output, which is most displeasing on lamps.

If several such engines are interconnected, excessive circulating currents may result.
broadgage is offline  
Old 27th Jan 2021, 8:04 pm   #38
Heatercathodeshort
Dekatron
 
Heatercathodeshort's Avatar
 
Join Date: Jun 2005
Location: Warnham, West Sussex. 10 miles south of DORKING.
Posts: 9,145
Default Re: Standardisation of Mains Voltages

My Nan lived in Havelock Road Wimbledon and was connected to the old 110v AC loop line.
It consisted of what appeared to be a 6mm lead covered cable that ran neatly along the back of the houses with the input to each house looped through the brick wall high up on the back kitchen wall. [My dad always wondered how the whole lot didn't go up in flames] The box used to receive a clout from a broom to stop it cycling!

It terminated into a solenoid and a single fuse. The solenoid was wired in series with the house lighting supply that was limited to about 150w. If you exceeded this load the solenoid would come into operation and the lights would flash on and off until you switched a light off lightening the load.
Nan's Philco 444 was run from an auto transformer that stood open behind the radio on a small oak table in the corner of the back sitting room fed from a 2amp socket, the only one in the house. The supply of course was only intended to be a lighting circuit.
The generating station was owned by Wimbledon Corporation based in Durnsford Road.

You could use as much power as you liked providing it was no more than 150W at any one time with a flat weekly charge of 2/6d [Twelve and a half pence]

My dad lived long enough to see the old 110v power station chimney felled in 1962. He died the following year.

I believe the old system fed terraced houses around the Wimbledon area including Raynes Park. One of my customers in South Road Merton had a transformer in a sort of rabbit hutch feeding the then dead system in his front garden. It was discontinued in 1961 and I believe it was installed around 1885. I have never been able to trace any reference to it on the Internet.

There are still lengths of wire and the solenoid boxes in front porches of houses in Haydons Road that were wired along the front rather than the back. I was absolutely fascinated by the system when I was a kid. John.
Heatercathodeshort is offline  
Old 28th Jan 2021, 12:15 am   #39
Graham G3ZVT
Dekatron
 
Graham G3ZVT's Avatar
 
Join Date: May 2010
Location: Greater Manchester, UK.
Posts: 18,676
Default Re: Standardisation of Mains Voltages

That made fascinating reading John,
Real social history, especially the bit about banging the box with a broomstick to stop the lights flashing.
I hate to think what that would have done to a fridge compressor, but I guess those that wanted a fridge got one from the gas showroom.
__________________
--
Graham.
G3ZVT

Last edited by Graham G3ZVT; 28th Jan 2021 at 12:21 am.
Graham G3ZVT is offline  
Old 28th Jan 2021, 10:10 am   #40
duncanlowe
Nonode
 
Join Date: Jan 2016
Location: Stafford, Staffs. UK.
Posts: 2,529
Default Re: Standardisation of Mains Voltages

I know that Nuneaton went through two changes. I was told this when we visited the local cinema projection room.

The original projectors were still in use, in the late seventies or early eighties. The cinema was built in the thirties. The projectors used arc as the light source, and were installed when the supply was DC. Later the town changed to DC, so a mercury arc rectifier was installed, along with a bank of resistors in 'the resistor room'. Later the AC voltage changed again and became the national standard, so a transformer was added. All of this was still in use.

I bought a house there which had 'interesting' wiring, again still in use. It was for lighting only. There were two ceramic fuse wire holders one for L and one for N. The isolator switch was two pole, by way of two single pole switches and a bit of wood joining the two toggles. I assume this was a carry over from being installed back in the DC era. I also think this had all been put in after the house was built since I also found the pipes for the gas lights.
duncanlowe is offline  
Closed Thread

Thread Tools



All times are GMT +1. The time now is 8:09 am.