Re: Early Unusual Transformer Design
We did iron and copper loss tests in the C&G electrical courses and a temperature test. We checked the workshop temperature (T1) and the transformer winding resistance at the beginning of the test (R1). After a hour on load, measured the resistance once again (R2). then used the formula R2 divided by R1, then minus 1 and dived that by .004.(Temp Co. Eff of copper).We had a thermo couple in the windings and it is surprising how accurate the simple temperature test is. Ted
|